Baxi luna 310 fi problem
Rickster
Member Posts: 2
Hi,
i am having problem with my Baxi luna 310 fi. i'd appreciated it if you can give me some help on my problem.
basically my boiler is working fine, but when it is set to heating mode,
for every 10 to 20 minutes, there is a weak spark (like only 3 sparks
instead of a lots of 'tickings' for a normal start) and no flame is lit,
then the fan or flue fault light comes on, 2 seconds later, fan turns
off, and a no flame fault comes on too. if i reset the boiler, it will
work until the aforementioned behaviour repeat, and i have to reset the
boiler again for heat or hot water.
i observed it a few times and below is the sequence of events:
- heating mode, after many times of flame off and ignitions to maintain water temperature for heating
- water temp dropped and trigered a flame on command
- rely on PCB clicks
- fan came on
- APS clicked, indication of pressure differences = fan worked fine
- PCB commanded spark
- weak spark, only 3 spark incomparison to many for a normal start
- fan or flue fault light came on
- no flame fault light came on
- 2 seconds later, fan turned off, APS clicked to indicate fan was off
if i reset the boiler, it will work fine until the above events are triggered.
i am having problem with my Baxi luna 310 fi. i'd appreciated it if you can give me some help on my problem.
basically my boiler is working fine, but when it is set to heating mode,
for every 10 to 20 minutes, there is a weak spark (like only 3 sparks
instead of a lots of 'tickings' for a normal start) and no flame is lit,
then the fan or flue fault light comes on, 2 seconds later, fan turns
off, and a no flame fault comes on too. if i reset the boiler, it will
work until the aforementioned behaviour repeat, and i have to reset the
boiler again for heat or hot water.
i observed it a few times and below is the sequence of events:
- heating mode, after many times of flame off and ignitions to maintain water temperature for heating
- water temp dropped and trigered a flame on command
- rely on PCB clicks
- fan came on
- APS clicked, indication of pressure differences = fan worked fine
- PCB commanded spark
- weak spark, only 3 spark incomparison to many for a normal start
- fan or flue fault light came on
- no flame fault light came on
- 2 seconds later, fan turned off, APS clicked to indicate fan was off
if i reset the boiler, it will work fine until the above events are triggered.
0
Comments
-
Marathon
Have you tried to call Marathon, the USA rep.? (800)461-4657
The last Baxi I worked on the fan was working and the fault lights would come on almost immediately. I finally tracked it down to a melted venturi in the flue.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
RE: Venturi melted
Hi,
thank you for the idea. but my Baxi works for a duration of about 15 minutes, then the faults come out. so i don't think it is the venturi in the flue. plus it works again if i reset the pcb.
i haven't contact any Baxi service people yet, because i know they will just ask me to change the pcb and see if the behavior is the same. and the pcb is kinda expensive for a try.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements