9 units

jrbayside
Member Posts: 81
need to vent a very long main, which valve do you guys recommend
ps the main gets hot until about 5 feet to where it turns to go vertical
ps the main gets hot until about 5 feet to where it turns to go vertical
0
Comments
-
How long is the main
and what pipe size is it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
9 units
2 inch main, runs @ 90 feet on the horizontal0 -
Vent it
with two Gorton #2 vents. This will get the air out in a super hurry!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
9 units
Hi guys, put in gorton #2 on the end of the main line, but still get no heat from the tee feeding the riser. Any suggestions?0 -
9 units
Hi guys, put in gorton #2 on the end of the main line, but still get no heat from the tee feeding the riser. Any suggestions?0
This discussion has been closed.
Categories
- All Categories
- 84.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3K Oil Heating
- 57 Pipe Deterioration
- 797 Plumbing
- 5.4K Radiant Heating
- 371 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements