Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
9 units
Options
jrbayside
Member Posts: 81
need to vent a very long main, which valve do you guys recommend
ps the main gets hot until about 5 feet to where it turns to go vertical
ps the main gets hot until about 5 feet to where it turns to go vertical
0
Comments
-
How long is the main
and what pipe size is it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
9 units
2 inch main, runs @ 90 feet on the horizontal0 -
Vent it
with two Gorton #2 vents. This will get the air out in a super hurry!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
9 units
Hi guys, put in gorton #2 on the end of the main line, but still get no heat from the tee feeding the riser. Any suggestions?0 -
9 units
Hi guys, put in gorton #2 on the end of the main line, but still get no heat from the tee feeding the riser. Any suggestions?0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements