Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

1" main pipe but use 3/4" taco circulator

heatingFun
heatingFun Member Posts: 84
I have a one zone 2-pipe hot water heating system. The main line is 1" pipe but the plumber installed a 3/4" taco 007-fs circulator. Is this required? Why not use the 1" taco circulator?

I am adding zones.  Should I do the same use 3/4" 007 circulator or use 1" circulator?

Comments

  • icesailor
    icesailor Member Posts: 7,265
    Circulators:

    A 007 circulator is the same whether it has 3/4" flanges, bushed down to 1/2" pipe to 1 1/2" flanges. It's the same circulator.

    Most installer will use flanges that are the same size as the pipe being connected to. Perhaps the installer didn't have a set of 3/4" flanges and no set of 1" flanges and it was cheaper for him to buy two, 1"x3/4" Reducing Couplings and a few nipples.
  • heatingFun
    heatingFun Member Posts: 84
    007 circulator

    Are you saying the 007-FS series circulator is always one size no matter the size of the flanges?
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,357
    Yes that is exactly what

    he is saying. Same pump, just different flange sizes. There are also different sizes of pumps that use the same size of flanges. Clear as mud right?

    In all sincerity, the pump needs to be sized for what the load is. The pipe should also be sized that way. The size is not an issue unless the heat load is higher than the pump can handle.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • heatingFun
    heatingFun Member Posts: 84
    007 series

    So that means the 007-FS can be replaced by 007-FS-IFC with no other changes.
This discussion has been closed.