larry
ljm3
Member Posts: 5
knight boiler stops running lockout comes up
saying gas pressue switch turn power off
hit reset goes right back 2 red screen
larry
any ideas0 -
larry
any ideas0 -
larry
any ideas0 -
None
other than the obvious.Pressure or the switch.0 -
No 24 volts....
If this is the newer version of their control, I think it is a dead or missing transformer.
Best to consult the factory.
ME0 -
Gas Pressure Switches
Larry,
Could you get us some more information? (We have learned never to assume.) Are there gas pressure switches installed? Have you bypassed them to confirm that they are out of tolerance? If not, place a jumper in the terminals to see if that error comes up again.
We certainly would appreciate the opportunity to help you correct this. Our 800 number is 800-722-2101 and our staff of Technical Support will need the model and serial number of this unit and then we will be well on our way to resolution.
Don't hesitate to contact me at prohrs@lochinvar.com if I can be of further assistance.
Best,
Paul0