vacuum breaker
RJ_4
Member Posts: 484
Peerless boiler, low press steam 2 psi 1 pipe. System has Hoffman boiler feed pump. The vacuum breaker on the boiler failed, boiler was in a vacuum, water level dropped, the boiler feed control had turned on the pump but water would not go into boiler ? After replacing vacuum breaker problem went away. I think I forgot what was going on here. Any ideas would be appreciated. 29 hp boiler / 50 gal boiler feed
Rick
Rick
There was an error rendering this rich post.
0
Comments
-
oh for gravity return
with gravity return, there is no problem with vacuum breakers or traps; and also no pumps, or electricity needed. can you convert back to the old way?--nbc0 -
vacuum breaker
I am a little stumped. I normally see vacuum breakers stick and the boiler will go into a vacuum as the steam condenses. At this point the the boiler vacuum sucks the water out of the boiler feed tank without any help from the pump. This often leaves my boiler overfilled.
Good luck,
Tim0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements