miller furnace
jim_160
Member Posts: 24
I have a miller furnace model M1 w/ horizotal heat exchanger. The draft is 0. Complaint of smelly blue smoke coming out of chimney. I checked pump psi= 100. I increased it to 140 and smoke cleared up. I still had 0 draft. I tore down burner ,fan, and plennums to expose heat exchanger. It looked fine. I snorkeled out exhaust tubes rapping them as i vacuumed. No soot build up. Put everthing back together, Still 0 draft! I went up on roof, exhaust vent is good condition and intake air vent is in good shape. My pump psi is 140-- pump cut-off is good --cad cell resistance around 600-800,-- ignitor good. It fires up and runs good but can't get draft. Should I be concerned
0
Comments
-
Are you sure your manometer is good?
Just asking....0 -
what
size nozzle are you running in the unit? And is it constant ignition?
Here is some set up info for Miller's unit
It is recommended that the Co2 and Smoke levels be
measured for maximum performance. CO2 readings should
be 10 - 11% for 66,000 BTUH furnaces and 12 - 13% for
86,000 BTUH furnaces. The Smoke should be N0. 0 on
the Bacharach Scale, and 0 to 0.02 negative draft over fire.0 -
nozzle size
Thanks for the reply
The nozzle size is .50 80 A. I did not do a combustion test. The pump psi is 140 and cut off is holding with in 10 %. Do I use the site port over fire for all combustion test?0 -
ignition
Sorry
The ignition is not constant. The pump is a clean cut style0 -
Miller
Did you pull the burner and fire-box out and check for scale build up at the bottom of the exchanger? And..........
Take a CO reading at the breach with the fan off and then the fan on. If it changes you have a crack in the exchanger.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements