One pipe venting.
targetman
Member Posts: 105
I want to try to balance out a system that I worked on today. The third floor does not heat well. The two main vents are both #4 quick vents. One main is 4 times the size as the other. The third floor rads are a mix of old Ideal Air vents? and #1A"s. What size vents should I consider?
0
Comments
-
Venting
It sounds like all the vents are pretty old and possibly on the small side. If you can give us the size and approximate length of mains, we can figure out how much venting capacity on each main you will need.
- Rod0 -
main
Unfortunately thats not possible. I can get rid of the old vents on the third floor. Change them to the 1A's like someone statred to do. As far as the main vent, I'm going to half to wing it. I don't know any distributors in my area that carry Gorton vents. What Hoffman vent has more capacity than the #4 quick vent? The second and third floors of this building are unoccupied and while remain so. The first floor is forced air. Therefore I don't have to nail it perfect.0 -
pexsupply?
try pexsupply.com
I've used them, great custoemr service, quick delivery, great prices. Not affiliated with them. Just a happy customer.0 -
I don't order the parts
The Boss orders the parts. He will only buy local.0 -
Vents
You'd probably be okay with Gorton #1 s though since you mentioned that they aren't available local to you and Hoffman is, Hoffman #75 would be your best bet for main vents. The attachment nipple on the 75 is 3/4" MPT or 1/2" FPT.
For the radiators Hoffman 1A s (adjustable) are a pretty good bet. If you want more venting on the radiators you will need to go to a Gorton # C or D or a Jacobus (Maid -O-Mist) # C or D
- Rod0 -
vents
Thanks Rod. I just purchased the steam venting chart available here for future use.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements