Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Tekmar 256...

I'm wiring in a tekmar 256... I am all set w/ 1 exception. where does the wire on terminal 7 go to on a taco sr 502? Boiler is a Biasi and just has a 4006 operating control. ty,kpc

Comments

  • Gary Jansen_4
    Gary Jansen_4 Member Posts: 77
    end switch

    7 has to make to 9 on the tekmar. Run wires from these terminals to the ens switch on the Sr. 
This discussion has been closed.