Adding radiators for a second zone on first floor
ivanator2
Member Posts: 39
I had a Unico System install, including hot water coil and a new boiler. It was all undersized. Contractor installed a Slant Fin 140K Finally got contractor to perform load calc and after much back and forth, he agrees it's too small.
He's agreed to install larger boiler and I pay cost difference. He also agreed to put in a second zone, which would be piping to connect radiators on the first floor. I find and buy the radiators.
I will try and match the BTU output of the old radiators. There were six on the first floor. Each had an EDR of about 12,500.
I need to make sure the piping is done right. Should it be 3/4 " to a supply manifold and 1/2 " pex supplies to the radiators, and 1/2 " returns to a return manifold, then 3/4 " back to boiler?
This would be a separate zone with zone valves and a separate thermostat.
He's agreed to install larger boiler and I pay cost difference. He also agreed to put in a second zone, which would be piping to connect radiators on the first floor. I find and buy the radiators.
I will try and match the BTU output of the old radiators. There were six on the first floor. Each had an EDR of about 12,500.
I need to make sure the piping is done right. Should it be 3/4 " to a supply manifold and 1/2 " pex supplies to the radiators, and 1/2 " returns to a return manifold, then 3/4 " back to boiler?
This would be a separate zone with zone valves and a separate thermostat.
0
Comments
-
12,500 edr?
12,500 edr at 180 supply water = 21,250,000 btu
do you mean 12,500 btu each?
If 12,500 btu, then 1/2 inch ID pipe to each is fine. I would run 1 inch ID to the manifold. 3/4 is right on the cusp.0 -
heat loss
Do the heat loss for each room and size the radiators accordingly. It's easier to do it right the first time.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements