new primary
sparkie
Member Posts: 52
in Oil Heating
Would the Honeywell r7284u be a good replacement for the 8184 control? Beckett af burner about 25 years old Warm air system. Would want to go to interupted ignition.
0
Comments
-
I'd use the R7184A
and add a delay solenoid valve to the line between the pump and the burner. This will give you cleaner starts and stops, which will reduce sooting.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
As Frank said
You will need to have some sort of fuel solenoid whether it be in the form of changing your fuel pump to a clean-cut, or add a solenoid valve on the pressure side of the pump. These controls will only work if it has control over the fuel as well as the ignition0 -
GenSys
The only primary I use any more is the Beckett GenSys primary. You can get them with no programing in them for a direct replacement for the 8184G or you can add a Beckett Clean Cut pump and do a pre and post purge system.0 -
me too
I agree with Mac on this one. Genisys is the only control we use.0 -
7284 replaced 7184
7284 replaced 7184 control. although you can still get the 7184.
7284u is a great control the beckett is nice too. but like the honeywell better
7284u does not need clean cut or oil valve to be used. although a clean cut pump would make it run that much cleaner
upon installing a 7284u you pick
language eng fren span
whats it on boiler furance water heater
valve on delay 0 seconds up to 2 minutes or something
trial for ignition 15sec is standard
valve off delay 0 seconds up to 8 minutes or so
spark on delay Y or N
spark on run Y or N
configure TT Y or N
number of retries 0 1 3 no limit
show error codes Y or N
then it asks to baseline test
exit setup Y or N0 -
Honeywell Vs Beckett
I have used the honeywell primary before. I like the Beckett GeniSys. The honewell does not give you cycle by cycle read outs of what is going on. It just here is your averages. The GeniSys does not need to be used with a Clean cut pump. You can use it as a direct replacement for the 8184G. You just get one with no pre or post purge programed into it. Then if in the future if the customer upgrades to a clean cut pump you can then use your display and program what ever you want into it. Plus the GeniSys does not have the display right there tempting the customer to make changes. Not to mention that the GeniSys runs a little lower in price. Oh and if you are using the GeniSys with a forced air system with AC you can get the AC ready kit and not have to put a fan center on.0 -
7284 vs beckett
After extensive research on both, im going with the Honeywell 7284u. Not going to install a clean cut at this time, but if i do i can change the set up on the control.
Also thinking about changing from a typical "off the bottom of tank gravity oil feed" to a top of tank suction line and use the Tigerholm flexible floating suction line and their anti-siphon valve. In addition to this im planning on installing duel spin on filters in the line. Has anyone used these items, and is it worth doing this? My reason here is more for environmental safety than anything else. Also would i need to use a tiger loop on both burners? (furnace and water heater)0 -
Tiger loop
I always like to use a tiger loop when running an over head line. With two burners I'd look at two tiger loop ultra's. That's a tiger loop with a spin on filter already attached to the bottom. Also remember to put the bypass plugs in the return side of the oil pump when running the returns to the tiger loop0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements