Planning a Funeral for a couple very old traps - Can they be saved?

elfie
elfie Member Posts: 266
There are two very old and rare Arco 911 (American Radiator) traps that have been found to no longer work (what a surprise after 60 plus yrs) - they are end of main traps.  One is pictured below.



They are part of an Arco Model K ultra low pressure trap less radiator steam system and  it may be a challenge to replace them.



Is there any chance these traps can be saved?  maybe when they are opened up, there may be an opportunity to repair them (doubtful any repair kits exist for this trap). 



and then what to do with the old traps after being replaced - maybe they have value?

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    pictures??

    where for art thou?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Rip traps

    Even if they have died, then let them lie in state in a glass case as has done Kim Jong il. Others would like to see them, and don't forget the pictures!--nbc
  • gerry gill
    gerry gill Member Posts: 3,078
    where

    are those traps discharging to? are they just dropping into a wet return? Can you take the picture from farther back?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • elfie
    elfie Member Posts: 266
    better view of trap

    here is a better view of trap and connections near floor



    it connects to an underfloor return. the return slopes down when it gets close to the condensate receiver, and there is a low point on the return that then goes up to the pipe connecting to the receiver.



    so it appears the underfloor return may have about a foot of pipe that is likely full of water near the receiver so the trap may not be able to vent air.  its an old vapor system and seems odd to have no air venting when connected to an underground return.



    a further complexity, a longstanding underfloor leak was discovered which may have served as an air vent.



    a key issue - can the trap be potentially repaired? and if not, how hard to size up a new trap.



    thanks
  • gerry gill
    gerry gill Member Posts: 3,078
    I wouldn't bother

    trying to repair that old trap, i would just replace it with a good quality modern f&t..this is a house correct? then i can't imagine anything larger than a 3/4 f&t being necessary..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • elfie
    elfie Member Posts: 266
    edited January 2012
    funeral planned for some traps

    thanks



    it will be a sad day when these historic traps are retired.



    the end of the steam mains (post trap) go down to an underfloor wet return and no sign of venting



    the underfloor return has a longstanding leak (expansion joint) and this may have acted as an air vent



    the dry returns in original installation were vented to an air eliminator



    its a puzzle how the mains were vented given that it was a gravity return system - maybe  the venting was handled thru the dry returns (its a ultra low pressure system)
  • Dave in QCA
    Dave in QCA Member Posts: 1,788
    edited January 2012
    Both traps look like they were added

    If I am picturing your building correctly, the piping at the floor level is a wet return.  Is that correct?  The drawing for the ARCO system indicated that both the steam mains and the return piping drip to a wet return below the water line of the boiler, no traps needed as long as pressure are low, 8 oz.



    That is interesting, because both of these traps look distinctly like the original piping was cut and the traps fitted in.  The trap on the steam main, obviously was done a long time ago.  However the trap on the return line looks much more recent.



    But, as I recall, you have all kinds of alterations on the return piping, a condensate pump set, etc.  All of the venting would have been through the return piping runs, above the water line, that connect to the old ARCO air elimintor.   But...  this system has had a ton of changes and its pretty hard to get a clear picture of what's going on.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com