Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Buderus GB142 Boiler Outdoor Reset Control Affect Indirect Water Heater Efficiency in Summer?
researchittodeath
Member Posts: 6
Hi! Just had a Buderus GB142 Boiler installed at my Wisconsin home and next week will be installing the matching ST-150 indirect water tank.
In the summer months when the boiler is not being used for heat, does the Outdoor Reset Control unit have anything to do with how efficient the water heating goes? I'm new at this Mod-Con stuff...having just replaced my old Burnham oil burner.
Also this boiler was just put in last week and I noticed they mounted the outdoor reset on the South side of my home where it will get sun every day the sun's out. Should I have them move it to a shaded location on another side when they come out to install the water tank? Thanks much for the help!
In the summer months when the boiler is not being used for heat, does the Outdoor Reset Control unit have anything to do with how efficient the water heating goes? I'm new at this Mod-Con stuff...having just replaced my old Burnham oil burner.
Also this boiler was just put in last week and I noticed they mounted the outdoor reset on the South side of my home where it will get sun every day the sun's out. Should I have them move it to a shaded location on another side when they come out to install the water tank? Thanks much for the help!
0
Comments
-
If its wired....
right the boiler will ramp up for domestic. Yes by all means move the sensor to the northside of the house. that was a mistake.0 -
second that
the sensor should be mounted on the north side and should not see the sun....0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements