Losing water

GTD
GTD Member Posts: 33
Hi i have a weil McLain 368st oil fired steam boiler, for about a week the boiler is losing water. The sight glass is no water. Nothing on the floor, radiator don,t seem to be leaking . Any help would be great . Thanks tom

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    water loss

    this can be a dangerous situation!!. can you verify that your low water cut off is working?

    it may be only a plugged gauge cock on the sight-glass, do a search here for that term, and you will find instructions on how to remove the glass, and poke out the top and bottom connections.

    if you suspect a boiler leak, then the most certain test is to turn the boiler off, and add water until the boiler is over-filled above the top. verify that the water level rises in the sight-glass. then look for leaks on the floor over a period of several hours. don't forget to lower the water level when finished with the test.

    if you see water, then use the find a contractor button here to do a search by state, not by zip code.--nbc 