Vents on 2 Pipe System
BenEbling
Member Posts: 1
Howdy Gents -
1st time post for me. We bought an old century home in Columbus, OH. 10K sq ft, 2 pipe steam heat system with 30 radiators. My question - can I use air vents on this system? The steam traps appear to be working properly, but I'd like some of the radiators to heat faster than others.
Thanks,
Ben
1st time post for me. We bought an old century home in Columbus, OH. 10K sq ft, 2 pipe steam heat system with 30 radiators. My question - can I use air vents on this system? The steam traps appear to be working properly, but I'd like some of the radiators to heat faster than others.
Thanks,
Ben
0
Comments
-
2-pipe problems
Don't put vents on the radiators, as they were not designed to work that way. There must be some reason for any non-heating radiator. Have you checked the traps, thermostat location, main venting, and pressure. If the pressure is too high (sometimes more than 6 ounces!!!), the traps may not be able to do their job.--NBC0 -
its probably more likely
you have a steam distribution issue than an air vent issue.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
with 2 pipe
You can use the supply valves to throttle the radiators you don't want as much heat at. You should look into getting some books and reading up on steam, with a system that large I'm sure you'll have more questions. Take a look at these http://www.heatinghelp.com/products/Super-Deals/14/129/A-Steamy-Deal
I'm just a homeowner, and these are very readable and immensely helpful. If you can, take some pics of the boiler, and near boiler piping from as far back as you can, and any unusual looking things attached to the piping. I'm originally a Canton girl myself, sounds like you've got yourself a great new home, welcome aboardThere was an error rendering this rich post.
0 -
Post pics please
Do you know what kind of system you have?
Please post pics of some of the radiators, inlet valves, outlet traps, boiler, other devices in the boiler room, etc.
You don't indicate that there is anything wrong with the system, but that you want some of the radiators to heat faster than the rest. Are you saying that they already head evenly?
If you are trying to create a warm spot in your house, you could partially close all of the inlet valves except for the radiators that you want to heat fast. It would be a trial and error process, but it would probably work.
We really need pics and more information to advise.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements