Hartford Loop
Jim Pompetti
Member Posts: 552
Is there a steam boiler maker , that either suggest or insist , the installation of a Hartford Loop. I know all direction call for one . I have a plumbing inspector that says it is NOT necessary. You input needed.
0
Comments
-
Here is one without a hartford loop
Burnham commercial, for their boilers set up with a boiler feed pump are shown as not requiring a hartford loop. see page 38 at this link. http://www.burnhamcommercial.com/products/forced-draft-boilers/v9/io/manual.pdf
Hoffman specialty, shown at the top of page 3 in the following publication indicate that a hartford loop is not necessary on a dry return system. http://completewatersystems.com/wp-content/uploads/2011/05/7250.pdf
These are the only 2 exceptions that I am aware of, but there are probably more manufacturers that would agree with Burnham regarding a feed pump system.
On gravity return systems, where the I&M manual shows "minimum piping requirements" for the installation of a boiler, and that diagram shows and describes the pipes sizes and connections of the hartford loop, it would seem to me that the language is stating that the Harford loop is required by the manufacturer.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements