staple up snafu
BrianP
Member Posts: 1
I have a staple up floor warming installation that needs more btus to keep up would increasing flow ( larger pump ) increase btu output. insulating contractor did nor insulate under tubing.
0
Comments
-
What is
supply temp to the floor?
Staple up usually requires a higher temp to deliver btu's b/c transfer rate is lousy.0 -
How do YOU spell SNAFU????
I spell it S T A P L E U P. Pronounced Situation Normal, All eFed Up.
Increasing flow won't help much. Raising the temperature won't help much, other than causing the areas below the SNAFU to over heat.
Contrary to popular opinion, heat, in the form of thermal energy WILL flow downward, and even horizontally, through the path of LEAST resistance. The old adage of "Heat Rises" a[plies to hot fluid convection patterns. NOT radiant energy.
You MUST have insulation below the heat source. If it was speced and the insulation contractor missed it, he either owes you a fix, or money back.
METhere was an error rendering this rich post.
0 -
Boy did I
misread the first post.
Like Mark said, insulate under the tubing.0 -
Heat Goes Down
I installed Watts onyx tube thru out my freezing floors. I had a company install regular paper back insulation with no reflective barrier. My hope was that I would keep the basement nice and toasty while taking the chill off the floor, and it does. While the insulation will help you dramaticly I have had my best results with the bubble wrap duct insulation you can buy right at menards or home depot. Cut it to fit snug and this will help out tremendously. That is our standard install on our geo staple up floor warming applications and it works wonderfully.0 -
By Chance...
...did the contractor install aluminum transfer plates with the application?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements