main vent questions
MJ_in_centralPA
Member Posts: 20
I'm planning on putting in a main vent on my neglected unvented main steam line which is <strong>68ft long 2 1/2".</strong>
My father in law was planning on coming down to weld on a<strong> 3/4" tap</strong> 15 in after last riser and I was planning<strong> 2-3 maid o mist main vents menora style</strong> (based on my cu ft calculations)
Sound appropiate. <strong>Do I need a 3/4" tap</strong>? Thought i read some where that 1/2" tap is too small to vent my line in ~3minutes.
Thanks
My father in law was planning on coming down to weld on a<strong> 3/4" tap</strong> 15 in after last riser and I was planning<strong> 2-3 maid o mist main vents menora style</strong> (based on my cu ft calculations)
Sound appropiate. <strong>Do I need a 3/4" tap</strong>? Thought i read some where that 1/2" tap is too small to vent my line in ~3minutes.
Thanks
0
Comments
-
A LOT of MOM's
It looks like that 68 ft of 2-1/2 pipe has 3.9 cu ft of volume and a Maid o Mist #1 is rated for 0.33 cfm at 1oz of pressure so it will take a few of them. It might cost less to use Gorton #2's which are rated at 1.1 cfm at 1oz of pressure. Gorton #2's have a 1/2" male thread so you will need reducers if you build the piping with 3/4" and they are pretty large - make sure you have room for them
A 1/2" open pipe is good for 2.6 cu ft according to my chart, 3/4 would handle a lot more but I'm not sure you will need it but if your going to the trouble of welding something up why not? Just make sure you new tree will let any water flow back into the main so the vents don't spit or start acting like fountains.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
You're thinking of 3-inch pipe
2-1/2" has .030 cubic feet per running foot. So that main has 2.04 cubic feet. Two Gorton #2 vents are the right choice here, and a 3/4" tap as proposed will work fine.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
maid of mist
thanks so much guys for your quick responses
could I use maid o mist? what is the rating on maid o mist ?0.33cfm at 2oz?
what is gorton #2 cfm at 2oz?
maid o mist is much cheaper than gorton#2, how many maid o mist would i really need 6 maid o mist #1's?0 -
cfm comparison
Maid O Mist #1 is 0.590 cfm @ 2 oz.
Gorton #2 is 1.750 cfm @ 2 oz.
Three times the vent for only twice the price.
Here is a shortcut to some more information (pictures and a video) http://www.gwgillplumbingandheating.com/webapp/GetPage?pid=4150 -
I prefer
to size main vents at 1 ounce. At that pressure the Gorton #2 will vent 1.1 CFM.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Why is it preferable
to size the vents at 1 oz.? Sure does makes the math easier. 2.04 cu ft needs 2 vents. 3.06 cu ft would need 3 vents? 4.08 cu ft would need 4 vents? 5.10 cu ft would need a 1" tapp? Or am I not looking at this correctly?0 -
If you size main vents at 1 ounce
riser vents (if used) at 2 ounces and radiator vents at 3 ounces, the steam is more likely to fill the mains first, risers second and rads last.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks
I had forgotten. You explained that to me before.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements