Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Heat Load Calculation
I am doing a heat load on a new house and would like to know how to do a room with 2 1/2 walls to the outside and 1 1/2 adjacent to a garage and storage room that could see 30 degree temps (Fahrenheit). The inside temp is 70 degrees - outside is 0 degrees. How do I split the calculation?
0
Comments
-
Basics
Basics for figuring heat loss thru an outside panel
TI-TO divided by R-Value = btu sqft
TI = Temp Indoor
TO = Temp Outdoor
Wall is 10' long 8' ceilings with no windows or doors.
(70-0)/19 = 3.68 btu x 80 = 294.4 btuhr heat loss
( 70-30)/19 = 2.11 x 80 = 168.8 btuhr heat lossThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements