Odd steam problem
jjplumber
Member Posts: 2
Just replaced gas steam boiler (residential), sized boiler by sq ft of steam based on radiator sizing. Full 3" dual header with expansion loop connecting to two separate distribution mains. System was banging and upon inspection, looked like system was surging and throwing water into mains. Boiler was skimmed at installation and re-skimmed today. Added steam clean to system but with no avail. The odd thing that happened was when we shut boiler down, it started banging again and we opened boiler drain (on boiler) the system was in a vacuum and sucked air in and then started to drain. ANY SUGGESTIONS?
0
Comments
-
The system
water may still be dirty. Are the mains pitched properly and insulated? Are you sure near boiler piping is to manufacturers specs along with the Hartford Loop connection?0 -
Venting may be part of the problem
Under vacuum indicates to me a possible venting problem.
If the vents work, then air should have already been in the system. Also as Jason pointed out, may also be a pitching / water trapping issue and or a lack of a hartford loop.0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements