UPONOR 511S & TACO ZONE CONTROL WIRING
JDCOUNTRY
Member Posts: 2
Thought a simple project would be to replace a 2 wire battery operated thermostat...well now i'm lost. I have the UPONOR 511S and am wiring it into the TACO-ZVC406 zone control valve. SEE ATTACHED PICTURES.
The 511 needs to be wired into the zone 1 thermostat. The old thermostat only had 2 wires plugged into the ZONE 1 thermostat receptacle...but that's not going to work with the new one. If anyone could walk me through the wiring i'd greatly appreciate it!
Thank-you!
The 511 needs to be wired into the zone 1 thermostat. The old thermostat only had 2 wires plugged into the ZONE 1 thermostat receptacle...but that's not going to work with the new one. If anyone could walk me through the wiring i'd greatly appreciate it!
Thank-you!
0
Comments
-
t stat
get a simpler thermostat.
that one is for remote sensing0 -
24 Volts
You need to power the 511 via a 24V transformer and take terminals 5 and 6 on the 511 back to TT on the zone control. If you using this just as a thermostat make sure you program it correctly. It can be used to sense air, floor or a combination of both when using floor sensor for radiant. It will learn the zones cycle.
http://www.uponorpro.com/~/media/Extranet/Files/manuals/SetPt511s-512_InstHB_3_07.aspx?sc_lang=enThere was an error rendering this rich post.
0 -
Don't need a second transformer
Place a jumper from R to 5 in the thermostat and take 5 & 6 back to T-T in the ZVC, Take common back to the number 1 terminal on the zone valve connection strip. Number 1 is always common on the ZVC.
Tim D.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements