reduce a 2" return line to 1" pipe at repair then back to 2"
jef
Member Posts: 8
can i reduce a 2" return line in steam system to 1" for 4ft of repaired/replaced pipe and couple of 1" 90s then
back to 2 " return line
i am trying to repipe to back of concrete step instead of going thru concrete step as old pipe did
back to 2 " return line
i am trying to repipe to back of concrete step instead of going thru concrete step as old pipe did
0
Comments
-
Depends
It would depend on the radiators that are served by that return line. If you are able to measure the EDR of the radiators that would give us the necessary info. If not then you can post pics of the radiators. Include the height of each radiator.0 -
Even easier
Tell us the size of the boiler (In NET BTU or Sq.Ft. of Steam) and tell us if that pipe's handling all of the condensate or just part of it.0 -
240k well mclain
the repair is on line with 1/3 of radiators
other side of bolier line are served by the other 2/3 of radiators
approx 22 radiators 240btu boiler
bolier in middle of bldg with return line going on each side of boiler then coming into one return line feeding boiler0 -
No problem
Roughly speaking, you should have no problem. Try to flush that return out while you've got it cut apart. You won't believe what lives in them.0 -
return under steps
why not leave some means of temporary disconnection for future cleaning, such as a union on both sides of the steps. any part of the piping with a reduction in diameter is bound to collect debris.--nbc0 -
Insulate the copper pipe
If you're running the new copper pipe inside the old iron one, as a precaution, I would wrap the copper pipe in plastic electrical tape to isolate it from the old iron pipe.
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements