Honeywell m945
lchmb
lchmb Member Posts: 2,997
I am looking for an electrical schematic for this valve. Any chance someone has this?
M945A1017
  • bob_46
    bob_46 Member Posts: 813
    Valve?
    M945A1017 is not a valve number it is the number of a series 90 modulating proportional
    spring return motor that may be used to operate a valve. It requires 24V 40VA on
    terminals T and T the other three terminals will be labeled R,W, and B. Remove the wire from the R terminal and jump terminal R to W the motor should turn counterclockwise.
    Jump R to B and motor should turn clockwise. The motor is controlled by any number of three wire controllers that have a 135 ohm potentiometer in them. The motor is usually mounted so the spring return will drive the valve to the full heat position in case of power
    outage or failure.
  • lchmb
    edited December 2011
    thanks
    Bob, wrong use of words on my part. Was a long day but you gave me the exact info I needed!!. The motor isn't functioning on a loss of power and I couldnt remember which terminal's to jump in order to get it to open and close...