A gauge that works!
nz
Member Posts: 125
So reading on here inspired me the other day to actually get a gauge that moves, so I can see what my system is doing.
I carefully removed the old pigtail and elbow. I installed a new red brass pigtail (filled with water), red brass nipples, associated fittings, a 1/4" ball valve, a Ray Snubber, and Wika 0-3PSI gauge.
I was surprised to see that the system never got over 0.25PSI. It got to 0.1PSI when the steam reached the end of the mains (about 15 minutes), and 0.2 once the first and second floor radiators started filling. The system ran for about 45 minutes (my boiler input is 525,000 BTU/hr) to build 0.25PSI.
I also added some 3/4" brass pipe to the bottom of the low water cutoff cleanout, so I can be lazy and not lift up the bucket.
The 0-30PSI gauge is still there, but its behind the pressuretrol. It never moves. I was thinking I could add a vacuum gauge too - will that work on here, or should I add it near the main vent?
I have attached before and after pictures. I welcome your feedback.
I carefully removed the old pigtail and elbow. I installed a new red brass pigtail (filled with water), red brass nipples, associated fittings, a 1/4" ball valve, a Ray Snubber, and Wika 0-3PSI gauge.
I was surprised to see that the system never got over 0.25PSI. It got to 0.1PSI when the steam reached the end of the mains (about 15 minutes), and 0.2 once the first and second floor radiators started filling. The system ran for about 45 minutes (my boiler input is 525,000 BTU/hr) to build 0.25PSI.
I also added some 3/4" brass pipe to the bottom of the low water cutoff cleanout, so I can be lazy and not lift up the bucket.
The 0-30PSI gauge is still there, but its behind the pressuretrol. It never moves. I was thinking I could add a vacuum gauge too - will that work on here, or should I add it near the main vent?
I have attached before and after pictures. I welcome your feedback.
0
Comments
-
30# gauge?
Can you and the inspector see the 30# gauge that seems to be hidden behind the pressure controller?0 -
Vacuum gauge
You already have a vacuum gauge. The original 30PSI gauge is a compound gauge which indicates both pressure and vacuum. If you look carefully, the graduations below zero are marked in inches of mercury, which are units of vacuum measurement.0 -
Visibility
Yes, its not fully from the front - but the side it is.0 -
Looks good
If you wanted to see the 0-30, you could have the pressuretrol on the left. Is the wire long enough?0 -
P-Trol
Thanks...
I could move it, but it would be tight.
That 0-30 gauge doesn't work. Vacuum or Pressure. You can see the gauge if you kneel down (the P-Trol is actually a little higher than it). But I've watched this thing for the 18 months I've lived here, it has never moved a millimeter.
I would like to get a vaporstat and another gauge in OZ once I get the system balanced properly.0 -
code required gauge
As you know, the 30 psi gauge is required by code, but for atmospheric boilers it is generally useless unless you do have a problem... and if you have 5 pounds of pressure you would certainly want to know it. I am sure the gauge would move it you actually had some real pressure.
You're improvements look great!Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
3.0 psi gauge
My 3psi Wika gauge always ends up reading in the negative when the system is cold. I guess because the water won't let the slight vacuum that gets created as it cools release.
Are others having the same issue and simply re-zeroing the gauge or is a vacuum breaker necessary?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
My wika 0-5 lasted about 3 weeks
off a pigtail. It did however also go into the negative when the system shut down.
I dont really know if their that accurate.0 -
i have a wika 0-20oz...
and a digital pressure transducer (with 0.00 precision (a slight breeze of opening the door will change it's reading)) .. and they are spot on the same .. whether both are out or not, i can't be sure .. my wika is 2yrs old.
also .. i do have a valve (that I almost never open) to break the pigtail vacuum ..
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements