steambaseboard
davem1
davem1 Member Posts: 13
I have a one pipe steam system. Can I replace an old rad with 10 feet of baseboard without having to install a drip at the end. its a straight run that I'm sure I could pitch back to the supply. thanks davem
  • Steve_210
    Steve_210 Member Posts: 664
    Is it
    Cast iron BB with 3/4" tappings, if so the tapping would be too small to handle that amount of condensate.
    A friend once suggested using both tappings for supplies and use a larger supply pipe, but I have never tried this. Perhaps somebody else has. If it was me I would find a return and pipe it as shown in LAOSH
  • furnacefigher15
    furnacefigher15 Member Posts: 514
    venting is key
    If you can pitch even a little this will help.
    Don't put the air vent in the top, put it in the lower pipe tap opposite of where the steam feed will be.
    Be careful, use a radiation reference guide to size the baseboard to the old radiator and match output, or do a heat loss on the room, and add 20% for possible condensate blockage.
  • furnacefigher15
    also use both taps on one side
    Use both the upper and lower tapping for the supply feed on one side.
  • Mark N
    Mark N Member Posts: 1,148
    Baseboard
    According to the "Lost Art of Steam Heating" a 10ft length of steam baseboard would need to be pitched 5" to get the condensate to drain. It is recommended to pipe like it is 2-pipe then the pitch is 1" in 20ft.
  • kcopp
    kcopp Member Posts: 4,682
    another simpler option...
    are these... http://steamradiators.com/
  • davem1
    steambaseboard
    they are  5ft units with 1-1/4 inlets and outlets
  • davem1
    steambb
    there are no upper and lower tappings on baseboard units
    Steamhead Member Posts: 18,507
    If your present radiators are cast-iron
    you should replace them with cast-iron. Steel radiators like the ones at steamradiators.com cool off much faster than cast-iron, which can lead to discomfort.
    If you want a different radiator, why not use a cast-iron one of a different shape?
    Consulting
  • furnacefigher15
    Not cast Iron?
    I assumed you meant cast iron baseboard. I would not even try anything else. Cast iron whether its a radiator or baseboard is the only way to go in a residential situation using steam.
    Even if you could match the heat capacity, the steel or copper will cool too fast on an off cycle and leave that room continually off step with the pace of the rest of the system.