Getting heat with thermostat turned all the way down
StephenO
Member Posts: 6
I have a brand new Slant Fin TR-20 oil burner.The boiler sends heat with out any call from the thermostat when ever it kicks on. I changed the thermostat and it still happens. Only have one zone with circulatory pump.The boiler seems to be running fine shuts off when reaches high limit. In the Aquastat, when I get to the TT display for Local Thermostat Status it is displaying OFF is this the correct position and if not how do you change it. I am a new licensed oil technician and could use some help thanks.
0
Comments
-
let's check the settings first,
then the wiring.
When you say the boiler sends heat, do you mean the burner fires without a call from the thermostat? Is it because the boiler is also used for domestic hot water? It seems the circulator isnt running if the boiler shuts off on high limit.
What are the settings on the aquastat (hi low diff)?
How is it wired? where are the thermostat wires?, what wires are on what terminals?
After you answer these questions, they we'll talk about how to check out the aquastat.There was an error rendering this rich post.
0 -
Getting back to you
The high limit is 190. The low limit is 150. The diff is 10. The thermostat is wired to TT, the circ. is wired to C1 Black and C2 White. We are getting domestic hot water from the boiler.This was a package unit so most of the wiring was done.0 -
sounds like
you are getting gravity feed heat. What do you have for a flow check? Is it closed and seating? Is it an IFC pump? Disconnect "TT" from the aquastat, and let it set for a while. You will know if it is a thermostat problem, or ghost flow. Pics of your system will help us to help you0 -
Will check that
I can't get that information till tomorrow and I will take some pictures. Thanks for the help.0 -
You're welcome
hope we can get you some answers0 -
Gravity heat
It was gravity heat, put in a check valve in heats working good now.
Thanks again for the help
Steve0
This discussion has been closed.
Categories
- All Categories
- 86.1K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 84 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 62 Pipe Deterioration
- 905 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.7K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements