Primary/secondary piping
mike chacon
Member Posts: 17
On primary loop which includes my cast iron boiler, does position of primary pump matter if positioned before closely spaced T's (secondary loop) or downstream/after closely space T's ( primary pump >>>>>>>>Thanks mc
0
Comments
-
Doesn't matter Mike
So long as all pumps are pumping away from the expansion tank.
METhere was an error rendering this rich post.
0 -
Primary / secondary
The primary pump will be pumping away from expansion tank, the secondary pump I guess will be pumping away. Will the additional head from primary pump passing the closely spaced T's cause any issues with secondary flow. My desire is to have slightly more flow through primary/boiler loop to help boiler return water to come up/rise in temperature faster to help with boiler protection before majority of heat sucked away to secondary heavy radiator loop.0 -
Hey ME
How's the mountain house/flying saucer. Everything up/ working. Saw post on TV episode. Missed the show, hope I can see repeat on Comcast "On Demand.
Mc0 -
Nope
If piped correctly, both loops will be isolated from each other. The head in each loop is a function of pipe size & length, and the circ on that loop. On the boiler loop, plus loss thru the boilerThere was an error rendering this rich post.
0 -
Still doesn't matter...
Mike, The inlet to the secondary pump may see the higher discharge pressure from the primary pump, but the primary pump will still not induce flow through the secondary. For example, if the primary is capable of generating 10 PSI of pressure, and the secondary pump can only generate 5 PSI of pressure, then the secondary pump with a static fill of 12 PSI will see an inlet pressure of 22 PSI, but it (the secondary) can still only add 5 PSI, so its discharge would be 27 PSI.
Make sure that you have the proper amounts of straight pipe before and after secondary connections.
The Space Ship is moving along slowly. Waiting for the electricians to get done with their work so I can finish mine :-)
METhere was an error rendering this rich post.
0 -
Where are the magic formulas for pipe spacing?
Hey all,
I'm working on a longer post regarding primary secondary piping but I thought I would tack a basic question on this topic.
Is the proper spacing for piping from the primary circuit each supply tee has to be within 12" of the previous supply tee but not closer then 5".
Returns don't matter.
Are there other details to keep in mind?
Thanks,
Ben0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements