Ideas?
AFred
Member Posts: 81
I have a customer that just remodeled part of their house. My company did a few changes to their system; added 2 zones of pour over in-floor(one for each 2nd flr bath), zoned 1st and 2nd flr( 1st floor is all home run cast iron rad, 2nd floor still on the old mains), radiators in 2 of the spare bedrooms were removed and replaced with CIBB(2nd flr).
Heres the problem(2nd flr), the master br has a massive radiator and heats up right away, the other 3 bedrooms (2 with CIBB, 1 with radiator) don't start to heat up untill the master br is about 80*.
The boiler is about a 20 year old power vented weil, pump is on the return( it would take quite a bit to repipe that). It has a old b+g LR20(1/20 HP), I can't find info on the pump curve for that b+g.
Is it worth trying a higher head pump? What can I do?
They actually need a new boiler, but I don't want to have this problem with a new boiler too.
???Help
-Andrew
Heres the problem(2nd flr), the master br has a massive radiator and heats up right away, the other 3 bedrooms (2 with CIBB, 1 with radiator) don't start to heat up untill the master br is about 80*.
The boiler is about a 20 year old power vented weil, pump is on the return( it would take quite a bit to repipe that). It has a old b+g LR20(1/20 HP), I can't find info on the pump curve for that b+g.
Is it worth trying a higher head pump? What can I do?
They actually need a new boiler, but I don't want to have this problem with a new boiler too.
???Help
-Andrew
0
Comments
-
a couple things...
BTW the LR20 cross ref w/ a grundfos 15-58 (on high spd.).
I would add a TRV on the master bedroom rad. that way when it satisfies it shuts it off. A Grunfos Alpha (15-55) would also be a good addition as it will adapt the pressure to when the rad opens and closes.... thats a start.0 -
Follow-up
I closed the rad valve on the master br, put a Taco 0011 in place of that LR20, closed the by-pass a little more, and shot some fernox cleaner in it.
A few hours later I had one very happy homeowner on the phone.
-Andrew0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements