Feedback on Proposed Repairs
JStar
Member Posts: 2,752
5 year old 112MBTUH Steam Boiler. When it's fully fired up, the house sounds like a percussive orchestra. Bangs, whistles, sloshes, the works. Some of the 2nd floor radiators are panting like a dog. I find that the original piping is a bit off. The main bullheads into a tee and splits off in two straight lines. So, one side is pitched properly, the other not. The basement ceiling is barely 6ft. There is not enough height to repitch the main. I proposed converting it to a counterflow main. Rearrange the bullheaded tee and keep the properly pitched main untouched.
I draw up an estimate, head out to my next call, and then of course, I start doing my best thinking. The main is 2" with 4 1" take-offs. The whole system only has 6 radiators, all piped 1". Damn. This boiler has to be oversized. I get a chance to revisit the house. Measure up all of the radiators, add a generous 33%, and calculate a required input of 80MBTUH. So, it is oversized. By about 30,000. Great.
Now, I'm not so sure that the piping repairs are going to solve everything. They should still be done, but I don't want to be in the situation of being married to the system after making promises. So, what I'm looking for feedback on, mostly, is the predicted success of converting the main to counterflow. The connected radiation on the main is (If I remember correctly) 125 sq.ft. I'll be able to pitch it 2" over 10 ft. back to the boiler.
The sizing issue...well, that's being discussed by the higher-ups.
I draw up an estimate, head out to my next call, and then of course, I start doing my best thinking. The main is 2" with 4 1" take-offs. The whole system only has 6 radiators, all piped 1". Damn. This boiler has to be oversized. I get a chance to revisit the house. Measure up all of the radiators, add a generous 33%, and calculate a required input of 80MBTUH. So, it is oversized. By about 30,000. Great.
Now, I'm not so sure that the piping repairs are going to solve everything. They should still be done, but I don't want to be in the situation of being married to the system after making promises. So, what I'm looking for feedback on, mostly, is the predicted success of converting the main to counterflow. The connected radiation on the main is (If I remember correctly) 125 sq.ft. I'll be able to pitch it 2" over 10 ft. back to the boiler.
The sizing issue...well, that's being discussed by the higher-ups.
0
Comments
-
You need at least twice the pitch
on counterflow as on parallel-flow- 1 inch in 10 feet vs. 1 inch in 20 feet. So with a low ceiling like that, parallel-flow is the best way as the main won't hang so low.
Also with parallel-flow, the effect of an oversized boiler won't be as bad since it won't be fighting the returning condensate.
How about some pics?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
RE
Sorry, no pictures at this time.
If I keep the main parallel-flow, the dry return would be about 24" above the water line when it's all redone.0 -
Any way
to switch to a wet return?
If not, you can probably get away with a 24" "A" Dimension. We shoot for 28", but I've seen systems work fine with 18" if the pressure is kept low.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
RE
No way to make a wet return. I was thinking the 24" A-Dimension wouldn't be the end of the world. I was concerned about it because of the oversizing issue. I suppose that the labor involved in converting to counterflow, or fixing the parallel-flow is just about the same. Would make sense to keep it parallel to help the condensate.0 -
RE
Just remembered. The other part that bothered me about keeping it parallel-flow. The radiator run-outs are horizontal off the main for about 8 inches. And they are all grouped near the end of the main. I didn't want the condensate to slosh around near the end elbow and create problems in the run-outs.0 -
Shouldn't be a problem
as long as the water can drain into the return without backing up.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
RE
Thanks for the input. Sounds like we have a better plan now.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements