Having Trouble with a TT PS 60
Rich Davis_2
Member Posts: 121
Got a no heat call yesterday evening, I installed this boiler about a month ago, everything checked out at the time. In the start-up mode at pre-purge a 9 code comes up (burner blocked). Removed burner assy looks good, no signs of any particles or soot, blew off wilh compressed air and reassembled. No luck. Tried calling TT, they are shut till Mon.
Has anybody else had this problem? Any advice would be greatly appreciated. It's been warm during the day but gets pretty chilly in the evening. Would like to get these folks back on line asap.
Thanks loads
Rich Davis, 3m's
Has anybody else had this problem? Any advice would be greatly appreciated. It's been warm during the day but gets pretty chilly in the evening. Would like to get these folks back on line asap.
Thanks loads
Rich Davis, 3m's
0
Comments
-
error codes
soft lockout error code shows 9 alernating between boiler temp and "b" and two digit number.
What were they?0 -
Got Her Goin'
Thanks for the quick reply that got me headed in the right direction,0 -
Tell us what it was
so that we can all learn.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
TT
Glad I could help,
was it air bound or the pump?0 -
There Were Two Problems
The homeowner had tried to purge some air from the system, he had closed the supply and return valves to the boiler, which somehow caused to LWCO to to cause a soft lockout b-26. And then my lack of knowledge not to realize that it was a 9 indicating a soft lock out, not a 9 as a burner problem and I mistook the b as a 6 (reached set temp). As soon as I opened the closed valves everything was fine. Hopefully I'll learn and remember from my mistakes. I'm not to sure about the remembering part.
What is your trick for removing the blower unit from the top of theHX/burner, as there is a mounting screw right under the blower motor.
Thanks again for the replies
Rich Davis0 -
A very long screwdriver
12" ought to do it. I actually got one with a blower kit I ordered; not sure whether they come standard that way because another blower kit didn't have one. Remove the top access panel, of course.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 102 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements