pressure problems
Boombadi1
Member Posts: 4
i have a oil fired v series burnham which is a hydronic pressure builds while sytem is heating causing relief valve to blow i replaced both the relief valve and expansion tank and im still having the issue also check feeder and it seems to b working and not overfeeding boiler any ideas ?
0
Comments
-
Is the boiler doing DHW also?
Could be a pin hole leak in your coil. Shut off the make up water, and if pressure stabilizes, its your pressure reducing valve, or another problem related to pump location in relationship to the expansion tank and the make up valve.
If that doesn't work, and you are doing DHW with the boiler, turn the cold water make up to the DHW off overnight and see if the pressure stabilizes. If it does, your coil has failed.
METhere was an error rendering this rich post.
0 -
couple things
X tank to small for system could be one. Unless that size has always been used trouble free.
To high system fill pressure. Fill pressure should be set will system is at ambient temperature. X tank should be set isolated from system.
If there is an indirect waterheater the heat exchanger could have a hole allowing domestic water pressure to raise heating side system pressure.
Gordy0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 102 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements