Correct Pressuretrol Setting for my EG45 Weil McLain (Gas) Steam Boiler
Ritzy
Member Posts: 34
in Gas Heating
What should the proper settings be on a Pressuretrol Device for an EG-45 Weil-Mclain (gas) steam boiler?
The most recent plumber who "tuned up" my boiler over the summer, moved the Pressuretrol's exterior, vertical calibrator to "1" and moved the inside white, horizontal, circular disc to "2". Now, the 2nd floor of my house doesn't seem to get enough heat and the boiler shuts itself off quickly.
Should the settings on my Pressuretrol device be adjusted further?
Thanks so much!
P.S.- I have had the two (2) main basement vents changed on the overhead
pipes, thinking that would help. I remove a bucket of water from the
boiler 1x a week during the heating season.
The most recent plumber who "tuned up" my boiler over the summer, moved the Pressuretrol's exterior, vertical calibrator to "1" and moved the inside white, horizontal, circular disc to "2". Now, the 2nd floor of my house doesn't seem to get enough heat and the boiler shuts itself off quickly.
Should the settings on my Pressuretrol device be adjusted further?
Thanks so much!
P.S.- I have had the two (2) main basement vents changed on the overhead
pipes, thinking that would help. I remove a bucket of water from the
boiler 1x a week during the heating season.
0
Comments
-
Try this
One learner to another, I've turned mine way down and it's working better than ever.
As I understand it, yours will go to 3 pounds, stop and drop to 1 before starting again. Try 1.5 on the outer dial on 0.5 on the inner. Works here, it goes to 2 and drops to 1.5 before starting up again. I'm going to try dropping the 1.5 setting lower over time.
I also had to clean out the pigtail to get mine working. Was overlooked at the annual service for years, and was blocked with crud. Worth checking out sometime, but it seems yours is working.0 -
I would
Post this in the strictly steam section. Your system should run perfectly fine on 1 PSI of pressure or less.
My EG-45 never even sees more than 0.5 psi and she heats the whole houseSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements