Gravity to pump conversion
steveo1
Member Posts: 8
I am getting ready to convert a gravity water boiler over to a KBN condensing boiler with primary/secondary piping and a side arm tank.
How do I keep the heat from migrating in the heat pipes when a call for domestic hot water?
How do I keep the heat from migrating in the heat pipes when a call for domestic hot water?
0
Comments
-
If you pipe it per the manufacturers drawings...
it won't be an issue. Use the "prioritized" DHW option and you will not have any problems. THe quantity of of heated fluid left in the boiler is nil and will not significantly affect the balance of the heating system.
Make absolutely certain that the pump you use for the DHW circuit has a check valve, either integral of external. In fact, just in the interest of potential mechanical (integral check valve) failure, I'd suggest also installing a spring check valve on the return between the tank and the boiler.
Congrats on your selection of heating appliances. Great choice IMPO.
METhere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements