How Much Water
KSKI3718
Member Posts: 4
<span>I have a Weil McLain 678 boiler on a job with flooding problems. As part of troubleshooting I called the Mfr. for the amount of water in the operating range of the boiler, the tech I spoke with did not answer (or understand) the question. Is there an accurate way to estimate the operating range water volume by dimensioning the boiler?</span>
<span>Thanks for your help.</span>
<span>Thanks for your help.</span>
0
Comments
-
Steaming Capacity
The manufacturer's data should show the steaming capacity.
If it doesn't and you know the "lowest permissible water level," just drain the water out of it into a bucket from its normal operating level to the lowest level and measure the water in the bucket.
If you don't know either, I'd measure the water content, using the drain-it-and-measure-it method between a 3/4-full sight glass and 1-1/2" from the bottom of the sight glass.
Ed in Long Beach0 -
Flooding Problems
Hi- What's causing the flooding problems? Does it have an automatic water feeder? Does it have a domestic HW coil?
- Rod0 -
Thanks
Ed,
Thank you for the info.
Rod,
I think this has been a problem since the boiler was installed 15 years ago replacing 2 higher water content boilers but there is also a chance that clogged returns are contributing to the problem. The feeder only went in 2 to 3 years ago. before that a caretaker fed and drained the boiler as needed so it was not noticed.
0 -
Page 31
I think page 31 might have the answer to your question. http://www.weil-mclain.com/en/multimedia-library/pdf/weil-mclain-pdf/products/discontinued/discontinued-boilers/78-boiler/78manual.pdf0 -
the great flood
we had that problem, with luckily no auto/over-feed to cloud the issue. we had several horizontal pipes just above the normal waterline of the return which hid the water as the boiler built moderate pressure [pushing water into the returns]. when we cut them out, and dropped all the wet returns to the floor, the problem was solved.--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements