thermostat problem?
rcrit
Member Posts: 74
I got a shiny new boiler last week and it's been in the high 60's ever since so I haven't had much opportunity to see it in action.
I heard the burner come on this evening (think jet engine) so I went downstairs to time how long it took to make steam and then get to the end of the mains.
After 5 minutes the burner cut off. It hadn't made steam yet and wasn't under any pressure. The header was starting to get warm but neither of the mains were warm at all.
Is this a case of a confused thermostat? It is an old mercury model and setting the temperate is more art than science. It is set to come on somewhere between 69 and 73. The temperature coil is hosed on it but other thermometers show it is ~72 inside.
I wonder if this is an anticipator issue. With my previous boiler it was set to the max, .8. It is currently around say .4.
I heard the burner come on this evening (think jet engine) so I went downstairs to time how long it took to make steam and then get to the end of the mains.
After 5 minutes the burner cut off. It hadn't made steam yet and wasn't under any pressure. The header was starting to get warm but neither of the mains were warm at all.
Is this a case of a confused thermostat? It is an old mercury model and setting the temperate is more art than science. It is set to come on somewhere between 69 and 73. The temperature coil is hosed on it but other thermometers show it is ~72 inside.
I wonder if this is an anticipator issue. With my previous boiler it was set to the max, .8. It is currently around say .4.
There was an error rendering this rich post.
0
Comments
-
hosed thermostat
if part of it is non-functional, then maybe the whole thing is too tired to work properly. the nice thing about the new honeywell digital thermostats is the setup--1cph for steam. there is no longer any fiddling with a tiny lever, while looking at minuscule numbers on a discolored piece of metal. when you feel the need for a little extra warmth, then setting up 1 degree on the readout will do the trick, and the reverse for a bit less warmth.
make sure that you verify on the package that the thermostat will do steam. most of us like the honeywell visionpro, which is a bit more expensive than the other h/w stats, but does a nice job.
otherwise, do a search here for "anticipator + honeywell", and you should find many recommendations for the setting of your old one.--nbc0 -
now that you mention it
As luck would have it I ordered a Honeywell TH5110D1006 this morning.
Maybe my current thermostat found out about it and is pouting :-)There was an error rendering this rich post.
0 -
anticipator
My guess is because your anticipator is set so low, it got hot enough to turn the thermostat off before the boiler made any steam.
0.4 is most likely WAY too low, 0.8 sounds more like what it should be. I'm currently fighting with the opposit. I had mine on 0.8 and the termpature shoots past my setting so I just dropped the anticipator down to 0.7. I guess only time will show what it actually did.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Antisapation of Antisipator Setting
Remove the t'stat from the subbase, remove the "w" wire from the subbase, have a pre-formed piece of wire ( 18-16-14-12-10-8-6 gauge ) with 10 loops, with your AMP Meter(everyone has one ,right?) on the 10 loops ,connect one end of the "multiplier" to the "w" wire,connect the other wire of the "multiplier" to the subbase "w" screw terminal. The AMP reading is ,say, 6amp,then set the antisipator to .6. Some systems may have a higher "start" amps ,then it goes down to the normal amps. Then fine tune!0 -
For sale?
How old is the old thermostat? I might be interested in buying. What is the model # ?0 -
tweaking
I ended up putting mine back on 0.8 and now to 1.2A. The system seemed to stop making steam just as radiators started to got hot.
I'm wondering if this is why Honeywell said to use 1.2 for steam, because the anticipator doesn't take time to steam into consideration.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
model
It is a Honeywell 822D. It came with the house, I've been here two yearsThere was an error rendering this rich post.
0 -
Too new
I'm looking for something old, glass, and brass.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements