Anyone Know?

xxxxxx
xxxxxx Member Posts: 7
I recently encountered a oil fired hot water boiler, expansion tank has been replaced less than one year ago and appears to still be doing its job. However 3/4 blowoff valve gushing water every time i attempt to add water to boiler (1-3 psi on gauge on front of boiler at most.) Am i making this harder than it has to be ? Replace valve should solve problem or is there more to this than meets the eye? Any and all help greatly apprciated.Also flocheck valve near exp. tank piped on riser in closed position does this have anything to do with press. problems in the past, vents on baseboards appear not to have benn touched in quite sometime????

Comments

  • billtwocase
    billtwocase Member Posts: 2,385
    is

    the expansion tank between a flow check and zone valves? Sounds like that's the case. If so, open the flow check. The zone valves will stop the natural convection. 
  • xxxxxx
    xxxxxx Member Posts: 7
    anyone know 2

    no zone valves in the equation
  • meplumber
    meplumber Member Posts: 678
    Could just be a bad tridicator.

    I don't trust these tridicators nowadays. They are making them cheaper and cheaper. Rig up a gauge with a boiler drain and verify that the tridicator is showing the correct pressure.
  • xxxxxx
    xxxxxx Member Posts: 7
    pt.3

     im watching gauge needle move each time i attempt to add water from fill valve
  • Ed N.Y.C.
    Ed N.Y.C. Member Posts: 73
    xxxxxxx

    Watching it move  and/or knowing its bad are not the same thing. You must test pressure in boiler . Get a hose x 1/4" adaptor and 100 psi  gauge and put it on working draw off and see what pressure is. now you have a place to start. not the same or very close then you know if gauge is bad. now you are ready to trouble shoot. ED N.Y.C.
  • Steamhead
    Steamhead Member Posts: 17,337
    Have you checked

    the pressure in the tank?



    If not, you will have to de-pressurize the system side of the tank all the way to zero. Then use a tire pressure gauge to check the pressure at the Schrader valve on the bottom of the tank. The pressure should match the system's initial fill pressure.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • xxxxxx
    xxxxxx Member Posts: 7
    Thank you all

    Thanks to everyone who offered any insight on dilemma. Much appreciated

    turned out to be blowoff valve, didnt have to replace the boiler fill or expansion tank

     however leak on cold water inlet to coil was a pain right along with the replacement of the tripple Aquastat withe the burned out board just below that leak. did i mention the T&P gauge just top left of that singed control,  stem snapped in threads of coil luckily there was an EZ out  just right for the job.

    tthanks again