30' main pitched back to boiler header

KBP&H_3
KBP&H_3 Member Posts: 67
We have this job (boiler torn out by others after basement was flooded) where 30 feet of the main pitches back to the header riser, As usual, We piped in according to Burnham IN5 specs, ,, any idea about all of this condensate coming back to the header???

Comments

  • Paul Fredricks_3
    Paul Fredricks_3 Member Posts: 1,557
    yep

    You have to deal with the condensate. Could this have been a counter flow system? Only 6 or 7 radiators? Then it needs to be piped correctly for that.



    If not, I've put a full size tee in the main just before it gets back to the header, and dripped in down to the return. Did the trick.
  • Rod
    Rod Posts: 2,067
    Counterflow Mains

    Hi- Just some visual to back up what Paul has suggested. The boiler pictured with the counterflow mains was done by Steve Gronski, a Rhode Island steam pro.

    - Rod