vaporstat and pressuretrol
MarkB
Member Posts: 4
Hi,
New to the board and thanks for the help. I already got a great bit of help.
I read all about the advantages of a Vaporstat (L408J 1017) over a Pressuretrol (PA404A) and ordered a Vaporstat just a bit ago but I have a question. It sounds like a silly but it's a safety question so I gotta ask.
The Pressuretrol documentation says it's a high limit safety control. Do I need both the Vaporstat and the Pressuretrol? If so do I just T it and install? Also is it plug and play with the two existing wires.
Thanks for the help and understanding,
Makr
New to the board and thanks for the help. I already got a great bit of help.
I read all about the advantages of a Vaporstat (L408J 1017) over a Pressuretrol (PA404A) and ordered a Vaporstat just a bit ago but I have a question. It sounds like a silly but it's a safety question so I gotta ask.
The Pressuretrol documentation says it's a high limit safety control. Do I need both the Vaporstat and the Pressuretrol? If so do I just T it and install? Also is it plug and play with the two existing wires.
Thanks for the help and understanding,
Makr
0
Comments
-
Use the Old Pressuretrol as a backup.
Hi- There is no such thing as a silly question! The Vaporstat serves exactly the same purpose as the Pressuretrol. It's just that the Vaporstat is designed to be operate more accurately at low (ounces per sq inch) pressure. Most people retain their old Pressuretrol and set it to cut off at 5 PSI. Set up this way it is a safety backup if the Vaporstat ever fails. Beyond that you have the safety valve which will blow off if the boiler pressure ever reaches 15 PSI. (One can't have too many safety "backups"!) If possible it isn't a bad idea to mount it on it's own port and pigtail so that if the other pigtail / port gets plugged the other will probably be free. On a lot of boilers a second port isn't available so you just tee the low pressure gauge and vaporstat and old pressuretrol off the same boiler port.
- Rod0 -
Thanks
Hey Rod,
Thanks again and I guess for the second time.
Mark0 -
Can I use an L408J on a 24V system?
The product data sheet shows contact ratings for 120V and 240V applications, but it's just a switch, after all. Am I right in assuming these will work with high or low voltage control circuits?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Yes
It will work with 24V.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements