Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
hot water zone off a steam boiler
Paul Fredricks_3
Member Posts: 1,557
How much hot water can you pull off a steam boiler? We have a customer with 3 zones and an indirect coming off a plate heat exchanger. They aren't getting enough heat transfer to make the hot water, especially if the zones are running. But if we put a larger plate heat exchanger on, will it keep the boiler from making steam?
I haven't been down there yet to scope it out, just trying to get some background info before I look it over.
I haven't been down there yet to scope it out, just trying to get some background info before I look it over.
0
Comments
-
RE
Typically no more than 30% of the steam capacity, or the added pick-up factor. The hot water loop should be an after-thought to the size of the steam boiler.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements