Vent doesn't seem to close on main riser
Options
Cahill
Member Posts: 4
I installed a Jacobus #1 main steam vent just before the riser.There had been one there that was plugged.It doesn't seem to close and it blows steam. How exactly is it supposed to function ? At what point should it close? Should it be blowing steam?
0
Comments
-
Leaking steam vent
Since it is new, I would check to make sure the vent is plumb. I would also check if dirt, pipe dope or teflon tape could have gotten inside the vent. Do you have any water hammer when the system fires up?
Good Luck,
Tim0 -
Vent blowing steam
Basic question.
What pressure are you operating the system at? Hopefully less than 2 psi.0 -
Problem solved Defective air eliminator vent
Maid of the mist #1 defective.It looks like another crappy product probably made by slaves in some third world country0