Converting from oil to gas Burnham V905A
thfurnitureguy_4
Member Posts: 398
My Burnham V905 calls for a Beckett CG 10-5s gas burner. I am trying to find the inlet gas pipe size. Can't find the info in any of the Burnham or the Beckett lit.
The burner requires a
minimum of 4.7 in hg pressure.
Burner input gas 808 MBH
about 15 feet between the main and the burner.
Is there a formula to figure this from the above info?
The burner requires a
minimum of 4.7 in hg pressure.
Burner input gas 808 MBH
about 15 feet between the main and the burner.
Is there a formula to figure this from the above info?
0
Comments
-
You need the over all length
of your gas lines. then there is a chart to use. You also need the total gas load for the gas lines. The size of the valve really means very little, you adapt to that right near the burner.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
FurnitureGuy!
Good to hear from you.
If I'm not mistaken, you can also get Carlin or PowerFlame gas burners for those units, and some of these may even have low-high-low firing which if set up right will save some fuel.
I'm working an out-of-town job next week but could investigate this when I return.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
oil to gas V905A Burnham
Hi Steam head! It has been a long time. I would like to know if there is a good alternative to the Beckett CG series. The one I am looking at is lo flame start only. I had thought about working up a control system to exploit this. Run the thing off a vapor control for hi lo flame and off at pressuretrol level hi pressure. I need to check if the Carlin or PowerFlame units will use the same mounting flange as my CF 800. right now the 2 Beckett units are interchangeable, on paper any way.
We changed the oil burner nozzle just before warm weather hit last year and it made a huge difference. The Boss is just burnt on oil bills and wants to switch to gas. If her calcs are right we should pay for its self the first season.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements