IBR baseboard ratings
DanHolohan
Member, Moderator, Administrator Posts: 16,601
<span><span style="color:#000000">I heard the
most recent IBR residential baseboard rating catalog has a “Table E” in it that you can use to take the
IBR tested data at 150F down to other temperatures such as 100, 110, 120, 130 and 140.
Does anyone have this Table E, and if so, could you share it with me? Thanks!</span></span>
most recent IBR residential baseboard rating catalog has a “Table E” in it that you can use to take the
IBR tested data at 150F down to other temperatures such as 100, 110, 120, 130 and 140.
Does anyone have this Table E, and if so, could you share it with me? Thanks!</span></span>
Retired and loving it.
0
Comments
-
RE
Not exactly what you're looking for, but I have this graph...
Just a few calculations get you the same numbers.0 -
Thanks.
I've got that, but I'm not sure if it applies to baseboard. When I heard about that new table I wanted to see if it agrees with what you've shared. Thanks!Retired and loving it.0 -
Don't know if this helps
but I use the Slant/Fin data
http://www.slantfin.com/images/stories/Technical-Literature/ratings_fineline30_r.pdfTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
That helps. Thanks.
Still love to see that new table if anyone has it.Retired and loving it.0 -
Table C?
Hello Sir.
I've searched for the illusive Table E and have never been able to find it.
I have found a Table C, which I'm sure you already know about.
But just in case:
TABLE C
Factors Used to convert I=B=R Steam Ratings to
Hot Water Ratings at Temperature Indicated
Average Radiator
Temperature Factor
100..............................................................................0.15
110.............................................................................. 0.20
120..............................................................................0.26
130..............................................................................0.33
140..............................................................................0.40
150..............................................................................0.45
155..............................................................................0.49
160..............................................................................0.53
165..............................................................................0.57
170..............................................................................0.61
175..............................................................................0.65
180..............................................................................0.69
185..............................................................................0.73
190..............................................................................0.78
195..............................................................................0.82
200..............................................................................0.86
205..............................................................................0.91
210..............................................................................0.95
215..............................................................................1.00
220..............................................................................1.05
225..............................................................................1.09
230..............................................................................1.14
235..............................................................................1.20
240..............................................................................1.25
http://www.ahridirectory.org/ahridirectory/pages/ftr/I=B=RFinnedTube.pdf
Peter0 -
That could be it.
Thanks much!Retired and loving it.0 -
-
-
very Interesting
Thank You Dan.
Notably lower than the Table C factors.
Peter0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements