Ok i just installed a new weil mclain steam boiler would like to replace the stock pressure with a vaporstat. Will the honeywell L408J work with low voltage? Literature rates the control contacts @120vac and 240vac. And was also looking for a better gauge for this boilet so i could read the pressure in oz of water. Thanks
0
Comments
-
Just a Switch
The Vaporstat is just a switch so it should work okay. You're better off using "high" (120V) voltage if you can as generally it is more reliable.
For a gauge go to the Gauge Store. http://www.gaugestore.com/products.asp?dept=1123
- Rod0 -
Has anyone wired a vaporstat into a gas boilet though the 24 vac circuit? ?????
So Rod are you saying to use the vaporstat to make and break the line voltage feeding the boiler instead of the 24 volt control circuit? Has anyone ran across this issue????0 -
Just Switches
If the Pressuretrol works so will the Vaporstat. Internally they are
practically the same - just switches. (Delete my comment on 24 volt
systems. I was thinking oil and I'm just not a fan of low voltage control circuits) If you don't have it attached the Weil
McLain EG comntrol supplement0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements