High co
Hardship
Member Posts: 5
in Oil Heating
Hi all, just a question on high co in a burner i was working on at the weekend. I serviced a boiler "a warmflow 50-70" with a Riello rdb 2.2 burner and on completion of the service i performed a test with the analyzer and i had to take it out of the flue because of a high co reading. I checked that every thing was right with the service manual ie. nozzle, oil pressure, air, but still i was getting a high co reading. I have come across this before and it was due to a slow running motor but the motor is fine on this unit, also i checked for excess air due to leaks but all seams fine. So any suggestions would greatly appreciated.
0
Comments
-
Maybe
the head adjustment is wrong?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
.
We see this every so often. Most of the time, if everything else seems right, it just needs a day to settle down. In that case I usually blame it on loose soot that the vacuum didn't get. When we first had the electronic kits we'd send someone back the next day and everything would be fine.
Other possible causes we have seen are air leaks between cast iron sections and a unit wet from condensation. No guarantees on those causes, but that's what we've seen.
If we get bad readings we double check everything. If all checks out we let it go. I think there are times when you will never find a cause.0 -
Riello RDB?
What country are you in?To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
High co
The country is Ireland.0 -
Good catch
Robert! I didn't even catch that accent!0 -
High co
LOL LOL ya guys im a paddy in hardship.0 -
How high?
What are the exact numbers? Excess air?To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
High co
The excess air is 26%.0 -
They're just bringing out the RDB in the States
so most of us haven't seen it yet. But combustion is combustion, so we need to check all the usual suspects.
If all the settings are correct, I'd look at the nozzle. It might look OK, but try another one to be sure.
One of these days I'd like to come to Ireland, to see the original Baltimore.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
High co
Well i did try two nozzles, but knowing my luck i could have two faulty ones so i will try a different one. As for the Baltimore West Cork i can tell you one thing for sure, its a hell of a lot different than Baltimore in the U.S. but its a very beautiful place even in the winter storms "and summer ones to". I have spent a lot of time in the states but never Baltimore, maybe someday.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements