Snow Melt system setup pex sizing
quantumkitty
Member Posts: 1
Hello,
I am in the works on a new construction home i am gonna move into the next few months. I have some knowlege on repair and installation of hydronic systems from working with my father, but I do have a few questions on my snowmelt design. I am not a mechanical engineer by any means ( I am a physics degee holder), so I do want to make sure all my numbers look good before I go purchase items.
I have a Peerless 95% efficency boiler. 199,000 BTU (I got this for free from my dad. its used but 3 months old)
I have 5 areas that I would want heated for snowmelt. Driveway, Garage Walkway, Front Walkway/steps, front porch, and back porch.
I am using 120 BTU/sq ft. Delta T falls between 20 and 30 degrees F
My main question is what pex size should I use on the driveways and porches
Heres my setup
Driveway 5 loops, 280 feet loop of 5/8" or 3/4" PEX
Porches are a total of 2 loops, 280 feet each loop. 5/8" or 3/4" Pex. Walkways: 2 loops 160 feet each loop. 1/2" Pex for sure.
I setup an excel sheet to calculate pipe resistance, head loss, flow and compared that to pump diagrams.
I think a B&G PL30 1/12 HP pump fits the bill no matter what size PEX I use (that and my father has a spare he is not going to use still in the box)
If I go with 5/8" pex on driveway and porches, I get 15.5GPM with a HL of 13 ft.
If I use 3/4" PEX, I get 18.7GPM with HL of 10.4ft.
I have taken into consideration the fact that a glycol mix will affect resistance and head loss.
What size pex for the 280 foot PEX runs, 5/8" or 3/4"
I am in the works on a new construction home i am gonna move into the next few months. I have some knowlege on repair and installation of hydronic systems from working with my father, but I do have a few questions on my snowmelt design. I am not a mechanical engineer by any means ( I am a physics degee holder), so I do want to make sure all my numbers look good before I go purchase items.
I have a Peerless 95% efficency boiler. 199,000 BTU (I got this for free from my dad. its used but 3 months old)
I have 5 areas that I would want heated for snowmelt. Driveway, Garage Walkway, Front Walkway/steps, front porch, and back porch.
I am using 120 BTU/sq ft. Delta T falls between 20 and 30 degrees F
My main question is what pex size should I use on the driveways and porches
Heres my setup
Driveway 5 loops, 280 feet loop of 5/8" or 3/4" PEX
Porches are a total of 2 loops, 280 feet each loop. 5/8" or 3/4" Pex. Walkways: 2 loops 160 feet each loop. 1/2" Pex for sure.
I setup an excel sheet to calculate pipe resistance, head loss, flow and compared that to pump diagrams.
I think a B&G PL30 1/12 HP pump fits the bill no matter what size PEX I use (that and my father has a spare he is not going to use still in the box)
If I go with 5/8" pex on driveway and porches, I get 15.5GPM with a HL of 13 ft.
If I use 3/4" PEX, I get 18.7GPM with HL of 10.4ft.
I have taken into consideration the fact that a glycol mix will affect resistance and head loss.
What size pex for the 280 foot PEX runs, 5/8" or 3/4"
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements