It's time to replace my 20 year old Burnham. It's attached to a Moline vapor system. We're looking at Burnham IN5, Weil McLain EG-40, or maybe a Utica MGB 100 series. If you Google reviews for each of them, it doesn't look good! I'm guessing it's because unsatisfied people are more likely to ****, and satisfied people keep it to themselves...



Is Burnham's cracking problem a thing of the past? Does Weil McLain really use rubber seals? I understand Utica uses cast iron push nipples. Any opinions from the pros are welcome.



-Wendell
«1

Comments

  • Joe V_2
    Joe V_2 Member Posts: 234
    i am a homeowner

    My opinion is to find the one that is closest to your radiator load. I have a Burnham IN5 and am very happy with it. it is reliable and on a Trane vapor system. My brother has a Pennco that he is very happy with on a single pipe system. I think the installer will have the largest impact on reliability and performance. The near boiler piping quality and correcting any wooly boogers out in the system will determine how the boiler does.



    Pennco is owned by Utica and Crown is owned by Burnham. There are likely to be more consolidations but truly, the installer will have a lot to do with how well a boiler will perform. Good luck!
  • moneypitfeeder
    moneypitfeeder Member Posts: 252
    homeowner as well,

    I have a Utica Peg 187 boiler, and I can't speak for the quality of other manufacturer's, but I have a few small gripes with the Utica. First there doesn't seem to be much insulation around the boiler.  The tappings for the risers are on the side, I'd prefer them to be on the top of the housing, as I've read it can make slightly drier steam. The damper motor has burnt out 4 times in 3 years (which isn't integral to the boiler, its a different manufacturer, but I question why they don't play nice together). And lastly, I know this is extremely nit picky, but, I'd like it to have had a tapping on the front to have the required 30 psi gauge mounted on the face to free up space on the pigtail for my low pressure guage, vaporstat, and ptrol. It would have been one less thing to balance on the pig. Good luck in your choice! 

    There was an error rendering this rich post.

  • ChrisJ
    ChrisJ Member Posts: 16,231
    I'm also a homeowner

    And I decided to go with a WM EG-45.  This is the same as the PEG-40 / 45 except it comes in pieces.



    I was also considering a Burnham IN5.  Truth is I think all of the boilers from any quality manufacture will work well when treated properly.  Whether its a Burnham or a Weil-Mclain, Smith or Slant Fin.  I also feel they will all FAIL just as fast when treated incorrectly as my Burnham V83 did as its previous owner ignored 3 serious leaks.



    I agree with Joe in regards to matching to your load.  There were two reasons I went with an EG-45 over an IN5 and they were the EG-45 has a lower water line and was easily avaliable from a local distributor.  The water line was a concern to me as the IN5 would have barely gave me 27-28 inches from my lowest steam pipe. The IN5 would be slightly undersized for my load but close enough in my opinion.

    As far as Weil-Mclain and rubber seals, I'm not concerned about it.  My understanding is they rarely fail and are far easier to fix than a push nipple if it does.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • lchmb
    lchmb Member Posts: 2,997
    I like

    the Smith with a power gas burner also. Seems to be a good combination, but of course as stated, the boiler is only as good as the install. Make sure whoever does it know's steam..
  • Wendell
    Wendell Member Posts: 61
    Not only steam...

    but vapor systems!
  • Steamhead
    Steamhead Member Posts: 17,314
    What boiler size

    do you need? Has anyone counted up the radiation on your system, allowing for any radiators that may have been removed? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Wendell
    Wendell Member Posts: 61
    edited September 2011
    The good folks at

    Charles Garrity and Son Plumbing sized my system. They recommended the Burnham IN5 and the Weil McLain EG40. I was wondering what other pros were using...
  • Rod
    Rod Posts: 2,067
    Boiler

    Charlie Garrity is a very experienced steam pro and he will recommend the size and model boiler which best suits your needs. You can consider yourself lucky that he is local to you. Good steam pros are hard to find!

    - Rod
  • crash2009
    crash2009 Member Posts: 1,484
    You lucky devil

    You can't go wrong with Charlie.
  • Wendell
    Wendell Member Posts: 61
    Thanks, Rod

    They actually gave me choice of a Burnham or a Well McLain. The rubber seals in the Well McLain made me nervous and was wondering what others thought.



    -Wendell
  • Wendell
    Wendell Member Posts: 61
    Yup!

    I was very impressed with his knowledge.



    Nice people.
  • Wendell
    Wendell Member Posts: 61
    Settled

    I just had a conversation with Charles and he put my fears of nitrile seals in a cast iron boiler to rest.



    We're going with the Weil McLain EG40.



    -Wendell
  • lchmb
    lchmb Member Posts: 2,997
    did anyone

    mention we like pics..Specially of a nice new steamer...;)
  • ChrisJ
    ChrisJ Member Posts: 16,231
    Nice!

    Great choice. The EG\PEG series of boilers have been around a long time and seem to be a really solid boiler.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Wendell
    Wendell Member Posts: 61
    Happy to oblige.

    Here's the before... after soon to follow.
  • crash2009
    crash2009 Member Posts: 1,484
    I have said it before,

    But I sure like how those returns are done. 



    How is Helge coming along?  You just about done?
  • Wendell
    Wendell Member Posts: 61
    I'm looking forward to floating...

    I work full time as an auto mechanic and only part time on the boat. I manage an honest two hours each night and several more on my one day off. My progress is slow, but I love it. The running joke among my friends is two more years until launch... I've been saying that for almost a decade.



    It's the journey, not just the destination, right?



    www.sshelge.com
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    We had a joke where I used to work.

    "The running joke among my friends is two more years until launch... I've been saying that for almost a decade."



    The first 90% of the job takes 90% of the time.

    The last 10% of the job takes the other 90% of the time.
  • Wendell
    Wendell Member Posts: 61
    Out with the old...

    .
  • Wendell
    Wendell Member Posts: 61
    edited October 2011
    New returns below the waterline...

    .
  • Wendell
    Wendell Member Posts: 61
    Piping complete...

    .
  • crash2009
    crash2009 Member Posts: 1,484
    Wow

    Looks good.  I am glad Charlie allowed the returns to stay.  Hope its not running, your King and Return Valves are closed :)
  • Wendell
    Wendell Member Posts: 61
    Yes, closed valves would be bad ;-)

    we're waiting on the electrician. The old Burnham was powerpile only (I will miss the old girl and her disconnection from the grid).
  • Wendell
    Wendell Member Posts: 61
    Finishing touch...

    auto-water and skim tap.
  • Wendell
    Wendell Member Posts: 61
    Skimming day

    Two hours per bucketful...
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,357
    Wendell that was my job.

    Guess I will find something else to do when I am waiting for the inspector. How did the water look? Was there much in the way of oil and pipe dope?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • lchmb
    lchmb Member Posts: 2,997
    nice

    job Charlie..you and your company do this buisness proud...
  • Wendell
    Wendell Member Posts: 61
    Hi there!

    Only a few specs of dope and minimal amounts of oil. The sheen gets thinner by the bucketful.



    I decided to skim it myself while we wait for the new chimney liner.



    No one will sign off on the cracked flue despite it's isolation by the fireplace support bricks.



    They agree with me that the crack is from the original construction 100 years ago, and that it's not causing a problem, but they're not willing to commit to it. That's understandable.



    We're steaming much quieter now than with the old battle-axe!



    I'll give you a ring when the new liner is in.



    -Wendell
  • Wendell
    Wendell Member Posts: 61
    Ain't

    that the truth?
  • Wendell
    Wendell Member Posts: 61
    What are the chances

    of finding parts for a Moline radiator valve. I was having trouble adjusting one of my radiators and found its "plunger" piece shattered. The attached photo points to an intact plunger from a different radiator...
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,357
    I have not seen any

    parts for them. Which radiator was it? Are all the parts still there? If you do not adjust it often an orifice of set size may be able to be used with a plain radiator valve.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,357
    Thanks.

    I had the whole "crew" on this one.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Wendell
    Wendell Member Posts: 61
    I was looking

    to shut down one of the two front hall radiators (foot of the

    stairway). I inverted the metering sleeve and it seems to have done the trick.



    These Moline valves are rather cleaver. They have interchangeable sleeves with slits cut into them. One simply balances the system by adding more or less slits to each of the radiators. Once balanced, you can only subtract heat from a room, not add.
  • Wendell
    Wendell Member Posts: 61
    Is it safe

    to grease the threaded portion of the plunger? (high temp. wheel bearing grease)
  • crash2009
    crash2009 Member Posts: 1,484
    Thanks for sharing the pictures

     of the metering sleeves.  It is nice to see what is inside.  Helps me appreciate the quality of The Moline System.  I noticed the four sleeves you showed have a different number of slits in each one.  Is it possible to just simply rotate the sleeve to adjust the amount of steam?  What kind of metal are they made of?
  • Wendell
    Wendell Member Posts: 61
    They appear

    to be made of brass/ bronze? They sit in a cylindrical chamber. Their rotation in the chamber doesn't affect the steam. When the valve is turned down, the "plunger's" edge closes off the slits. As the valve is opened, steam from underneath is allowed to flow through the slits into the chamber, then into the radiator. I'm guessing the system would originally be set up for even heat with all the radiators full open. If one gets too hot, less slits would be installed. The radiator at the top of the stairway had only one slit. Two radiators are at the base of the stairs... heat rises!
  • crash2009
    crash2009 Member Posts: 1,484
    I get it now

    When you turn the handle, the plunger moves in and out.  (I was thinking it rotated the sleeve) Thanks. 



    So you got some noise in there, and were thinking about some kind of lubricant, to stop the friction?  Is the noise the plunger rubbing on the inside of the sleeve, or something else?
  • Wendell
    Wendell Member Posts: 61
    No noise

    just a little sticky when being moved... a few of the valves require jiggling their handle to get the plunger to slide. The reverse screw clearances are sloppy (reversed so turning clockwise pushes the plunger down, making it more "natural" to adjust).
  • crash2009
    crash2009 Member Posts: 1,484
    What would

    Charlie think about using graphite?  We use it on valve stems everyday.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,291
    Why

    Why did you replace the Independence in the first place? 



    What was wrong with it? 