I have an oil fired Burnham Megasteam, 3 yrs old, and just had it serviced for the beginning of the heating season. The LWCO probe hasn't been removed and inspected/cleaned since the installation. While the service technician was doing his thing servicing the burner and vacuuming the chamber/flue, I asked about the probe. He said it's not necessary to remove the probe and clean it because it's a "self cleaning probe", and pointed to the label on the side of the LWCO cover to back up his statement. It did in fact state that on the label, and I didn't push any further, but what's the real scoop on these "self cleaning" LWCO probes? (McDonnell-Miller is the manufacturer). 

Comments

  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    "Self Cleaning" LWCO probes.

    I have an M&M RB-122-E probe type LWCO.



    Its I&M sheets say, in part,



    Test the LWCO annually or more frequently

    Remove and inspect the self-cleaning probe every 5 years

    Replace the probe every 10 years

    replace the LWCO every 15 years.