Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
How Good Are Probe LWCOs At Cleaning Themselves?
Options
Chris M_2
Member Posts: 65
I have an oil fired Burnham Megasteam, 3 yrs old, and just had it serviced for the beginning of the heating season. The LWCO probe hasn't been removed and inspected/cleaned since the installation. While the service technician was doing his thing servicing the burner and vacuuming the chamber/flue, I asked about the probe. He said it's not necessary to remove the probe and clean it because it's a "self cleaning probe", and pointed to the label on the side of the LWCO cover to back up his statement. It did in fact state that on the label, and I didn't push any further, but what's the real scoop on these "self cleaning" LWCO probes? (McDonnell-Miller is the manufacturer).
0
Comments
-
"Self Cleaning" LWCO probes.
I have an M&M RB-122-E probe type LWCO.
Its I&M sheets say, in part,
Test the LWCO annually or more frequently
Remove and inspect the self-cleaning probe every 5 years
Replace the probe every 10 years
replace the LWCO every 15 years.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements
