Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
How Good Are Probe LWCOs At Cleaning Themselves?
Options
Chris M_2
Member Posts: 67
I have an oil fired Burnham Megasteam, 3 yrs old, and just had it serviced for the beginning of the heating season. The LWCO probe hasn't been removed and inspected/cleaned since the installation. While the service technician was doing his thing servicing the burner and vacuuming the chamber/flue, I asked about the probe. He said it's not necessary to remove the probe and clean it because it's a "self cleaning probe", and pointed to the label on the side of the LWCO cover to back up his statement. It did in fact state that on the label, and I didn't push any further, but what's the real scoop on these "self cleaning" LWCO probes? (McDonnell-Miller is the manufacturer).
0
Comments
-
"Self Cleaning" LWCO probes.
I have an M&M RB-122-E probe type LWCO.
Its I&M sheets say, in part,
Test the LWCO annually or more frequently
Remove and inspect the self-cleaning probe every 5 years
Replace the probe every 10 years
replace the LWCO every 15 years.0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements