clueless but trying to learn

sgall
sgall Member Posts: 37
I am having an Alpine 80 installed soon and I am trying to make sure it goes well.  In the B&G guide Zoning Made Easy it mentions that in a 3 zone system any shared piping must be big enough to accomodate the shared flow.  The current piping for each zone is 1 1/4" and it is a monoflow system. What is confusing is that the boiler tappings are only 1".  Should my plumber do what the B&G guide says or are is your flow already restricted by the 1" boiler tapping size.  Thank you.

Comments

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,863
    Tapping size be damned...

    Most European boilers come with smaller tappings because they are assuming a different design temperature differential of the flow. THey use 30 degrees C, we use 20 degrees F.



    Size your distribution piping system for a 20 degree F delta T, then size the boiler interface piping for a 30 degree F differential and it should get you fairly close.



    ME

    There was an error rendering this rich post.

  • sgall
    sgall Member Posts: 37
    Thank you Mark

    for your reply.  The attached diagram is what the system will look like except I will have 3 zones instead of 2 as pictured.  I don't know if it was clear but this boiler is a replacement.  Just to make sure I am understanding you then it is okay to make the piping circled in black 1 1/2" while the system piping, boiler piping and IHW piping is all 1"?  Thanks again.