clueless but trying to learn
sgall
Member Posts: 37
I am having an Alpine 80 installed soon and I am trying to make sure it goes well. In the B&G guide Zoning Made Easy it mentions that in a 3 zone system any shared piping must be big enough to accomodate the shared flow. The current piping for each zone is 1 1/4" and it is a monoflow system. What is confusing is that the boiler tappings are only 1". Should my plumber do what the B&G guide says or are is your flow already restricted by the 1" boiler tapping size. Thank you.
0
Comments
-
Tapping size be damned...
Most European boilers come with smaller tappings because they are assuming a different design temperature differential of the flow. THey use 30 degrees C, we use 20 degrees F.
Size your distribution piping system for a 20 degree F delta T, then size the boiler interface piping for a 30 degree F differential and it should get you fairly close.
METhere was an error rendering this rich post.
0 -
Thank you Mark
for your reply. The attached diagram is what the system will look like except I will have 3 zones instead of 2 as pictured. I don't know if it was clear but this boiler is a replacement. Just to make sure I am understanding you then it is okay to make the piping circled in black 1 1/2" while the system piping, boiler piping and IHW piping is all 1"? Thanks again.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements