Sizing a new boiler to old radiators
stevelaw
Member Posts: 3
I have an oil-fired steam boiler (cast iron radiators) that's about 50 years old and operating inefficiently but with no trouble. I have been advised to get a new boiler. I have heard that in the case of steam heat it is more advisable to size the boiler to the existing radiator system. How is this normally done? This is a three story building with basement with a 50' x 35' footprint (ten foot ceilings), full underground basement, blown in insulation in attic, insulated on first floor but just plaster and lath on the second and third stories. The original boiler has a 472Mbtu/H plate on it.
0
Comments
-
sizing a boiler
Steam boilers are usually sized so the EDR (total area of all radiators) is equal to or less than the boilers Sq Ft of steam rating on the name plate. You generally need enough stem to fill all the radiators (or convectors) but you don't want to much more because that leads to short cycling which drives up fuel costs.
This chart will help you determine the sq footage of each section in your radiators. A section consists of a number of tubes or columns that are connected together, these sections are then connected to each other to make up the radiator.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
PDF not loading
For some reason the Boiler Sizing.PDF chart did not load. Lets try it one more time-
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
-
File
Thanks Rod, for some reason I could not get that same file to load with my post.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements