Polaris water heater Igniter?
PeterV
Member Posts: 1
I have a Polaris hot water heater, Serial # 0524107785. It's no more than 6 yrs old, and that seems to be a pretty low serial number. Anyway, the burner will not ignite, and it is blinking 3 times, which is supposed to indicate "failed ignition". The ignition module, a 'UT Electronic Controls 1018 Series Hot Surface Ignition' has already been replaced once, because the replaced unit was left behind! Is there a substitute ignition module, since I question the reliability of this unit. Could the problem be the actual ignitor? On a yellow tag in the module are the following numbers: 1018-525 3210560 0629.
0
Comments
-
ignitor
Test the resistance of your ignitor. Just because you have a failed ignition does not mean it's the control. You need to verify gas pressure's also...good idea to get someone trained in trouble shooting the unit to take a look.0 -
Polaris problem
Odds are good it's not the igniter but a gas pressure problem - typically you only need 3"w.c. to 14" which equates to 1/2 psi or LESS. If it's a propane system, check for turned off valves, crimped copper supply pipe, and the ever infamous empty tank...0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements