Wiring Truesteam Humidifier to Oil burning Furnace
MG_74
Member Posts: 2
Problem. We have a relatively new oil burning furnace and we are trying to install Honeywell Truesteam humidifier. We have had to put in a White Rodgers 8A05A-101 fan center transformer to allow furnace blower operation independent of heating. We have done that and put in a new Honeywell thermostat. We have the blower operating via new thermostat. All of that is fine. Still having trouble with the Truesteam not working. No warning lights flashing. Not sure if we have it wired properly to fan center? Truesteam does not seem to recognize power from from HVAC? Do we need a current sensing relay?
0
Comments
-
This should help
Low-Voltage Terminals
24V AC power for electronic humidistat.
HUM Low-voltage humidistat (or thermostat) terminals control humidifier operation.
C, R Connects to HVAC system transformer terminals (or relay transformer fan control R and C) to ensure HVAC power is present before humidifying. This can be disabled by changing DIP switch 4 (see page 16).
RT Connects to thermostat R terminal, which is normally switched to call for fan.
GT, GT connects to thermostat G terminal. GF connects to fan board G terminal. Thermostat G passes through the normally-closed (NC) relay contacts to GF, allowing fan activation. When TrueSTEAM is ready to provide humidity to the home, it will take control of the fan by forcing power from RT to GF (if not already activated).
EXT When a 24-vac fan board is not used to control blower (hydronic or cooling-only applications), this connection with GF provides dry-contact closure for fan calls. EXT/GF may be wired to a low-voltage relay control center to provide line-voltage fan control.
H and H go to your humidistat
R goes to R on your fan center
G on your fan center goes to GF
GT goes to the G on the thermostat
Then just hook up the transformer 24V to the 24V terminals. There you go. Good luck. Don't forget to push the reset button to ready the device.0 -
What about C?
Thanks for the post. I have had to wire in the fan center based on the wiring diagram that was provided. It called for wiring the two original 24v T T wires to the R and W conneciton on the new Honeywell t-stat we purchased. The fan center has a Com connection which I have assumed to be C which has been wired to C on the Truesteam and then another wired running from Com on fan center to C on thermostat. I think I have done the right thing. As for power to the fan center. It performs as a transformer as well and it is wired on its "hot" side to the power supply for furnace. The other "side' of the fan center is 24V with R,C (Com), G, W and Y. Are you saying I should wire 24V service to Truesteam from the fan center?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements